Anyone use VRF in an Auditorium/theater/lecture hall?
Anyone use VRF in an Auditorium/theater/lecture hall?
(OP)
Im working on a new building and we are considering a VRF system. The building includes a small theater (~200 people) and we are debating whether to provide a dedicated packaged DX system, or use VRF for this space. I wanted to see if anyone here has any experience with VRF systems in spaces with high load and ventilation diversity such as these. Also, how is the noise on the VRF fan coil units? Thanks!





RE: Anyone use VRF in an Auditorium/theater/lecture hall?
knowledge is power
RE: Anyone use VRF in an Auditorium/theater/lecture hall?
RE: Anyone use VRF in an Auditorium/theater/lecture hall?
how do you plan to match vrf controls with ventilation? that seems an issue to me - how to ensure minimum ventilation at low loads.
at first glance it looks more attainable to have separate ventilation diffusers
RE: Anyone use VRF in an Auditorium/theater/lecture hall?
RE: Anyone use VRF in an Auditorium/theater/lecture hall?
and depending on your distances you may be limited by refrigerant line length and ASHRAE 15 requirements. I would check those first.