circuit breaker choice

circuit breaker choice

(OP)
Hello everyone,
I wanna protect a 24V DC - 1A installation (the load is a relay). Can anyone please help me in choosing the suitable Circuit breaker ? And can I use a 250VDC CB in this case ?
Thank you.

RE: circuit breaker choice

What is the source of the 24V? A couple of little automotive batteries require a different solution to a large industrial system.

Why don't you want to use a fuse? Easier and cheaper for DC.

RE: circuit breaker choice

(OP)
Well, The 24VDC source is a digital output controlled by a PLC. This outputs are connected to a relay to activate scientific machines in labs. I can't use fuses because all the system is implemented on a rail.

RE: circuit breaker choice

By the system being 'rail mounted' do you mean the standard DIN rail or similar? If so, what about a regular DIN rail mounted fuseholder?

RE: circuit breaker choice

What are you trying to protect against? One option is a PTC fuse. This is solid state and resets. A nice option when installers are likely to make mistakes. These heat up and greatly change in resistance, a small current always flows to keep the device hot. All power must be removed for a minute or two for them to reset.

RE: circuit breaker choice

(OP)
@BrianG
Yes the system is DIN rail mounted. we have agreed on installing a circuit breaker. I have found one: Schneider CC60-DC 1A but 250VDC. I didn't find a 24V circuit breaker.
thank you :)

RE: circuit breaker choice

3
in the event of a short circuit you will probably find that the source of the 24V DC will shut down to protect itself long before the breaker ever thinks about tripping. That makes the breaker somewhat pointless. The breaker you propose (or the C60H-DC which is what I think you meant) is adequately rated for the duty but I don't know where the excess of current is going to come from.

RE: circuit breaker choice

(OP)
What if a short circuit occurs in the line between the relay and the 24VDC digital outputs?

RE: circuit breaker choice

If your 24V DC comes from a switchmode power supply the chances are it will shut down faster than the breaker will trip if a short occurs. I said that two posts ago. pc2

RE: circuit breaker choice

(OP)
What if the supply will not shut down? I am pretty sure that these outputs are not protected.
thank you

RE: circuit breaker choice

Post details of the supply. Saves us guessing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close