Area of coverage from overhead shield wires in a substation

Area of coverage from overhead shield wires in a substation

Area of coverage from overhead shield wires in a substation

(OP)
Typically, shield (static) wires are considered to provide a 30 degree cone of protection on either side of the wire. Can this value be increased for shield wires running side-by-side, at the same height above grade?

RE: Area of coverage from overhead shield wires in a substation

Yes

RE: Area of coverage from overhead shield wires in a substation

EVERY POINT of a well-bonded/grounded shield wire provides a cone of protection.

For a linear shield wire, this volume looks more like a triangular prism in the middle area.

Having two or more shield wires can give you overlapping coverages.

Just remember that you need to shield your equipment (and personnel) at the elevation of their tops, not just at grade.

This diagram should make it clear:

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources