Regarding Synchronous generator grounding and its effect on stability

Regarding Synchronous generator grounding and its effect on stability

Regarding Synchronous generator grounding and its effect on stability

(OP)
when do we go for NGR and NGT while grounding the neutral of the synchronous generator?

RE: Regarding Synchronous generator grounding and its effect on stability

Impedance grounding will limit the current in the event of a ground fault. The reduced fault current may avoid a destroyed generator core in the event of an internal fault to ground. The generator protection must be able to detect internal faults and and in most cases be able to shut down the prime mover. The fault current for ground faults external to the generator will be limited by the grounding impedance.
That said, if there are any line to neutral loads, the neutral must be solidly grounded.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Regarding Synchronous generator grounding and its effect on stability

(OP)
Thnx for ur reply.
on what basis do we select between an NGR and NGT for a synchronous generator?

RE: Regarding Synchronous generator grounding and its effect on stability

The stator core on a large set is a high value asset and the lower the fault current the better. Big machines generally use NGTs because they make it simpler to employ a physically rugged low resistance resistor in an arrangement which keeps the primary fault current to a few amps. The secondary current is generally large enough to drive a protection CT.

RE: Regarding Synchronous generator grounding and its effect on stability

Just add to ScottyUK's view; conventionally the relay connected to the NGT secondary side is voltage operrated. This makes the earth fault sensing more sensitive.

RE: Regarding Synchronous generator grounding and its effect on stability

(OP)
why cant we go for NGR?

RE: Regarding Synchronous generator grounding and its effect on stability

You can do whatever you want. It's just that people who have forgotten more about generators than you'll ever know have already figured out that a neutral earthing transformer is a better way to solve the problem. Plain resistors are really limited to LV applications.

RE: Regarding Synchronous generator grounding and its effect on stability

The OP didn't give a hint about the voltage of the generator. If it's LV, then a resistor. If it's at the low end of MV, then either is commonly used. For higher voltages than a few kV, then it's into the territory of NGT.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources