Hello,
We recently installed a piping network in which there are several gate valves.
All gate valves are socket welded, 1500#, SA-105, metal seats, less than 2'.
Fabricated and tester as per ASME B16.34 @ API-598.
Operating conditions: 1500psi@520F
A few valves have shown some leaks during operation. My customer told that those leaks are not acceptable and asks for perfect tighness of all valves.
My question for you guys are the following.
-Are my customer request realistic?
-If it is not realistic, is there official documentation stating maximum leakage during operation?
API-598 & ASME-B16.34 indicates zero leakage during testing for those diameters, but it is only for 15 seconds, at cold temperature. Does those tests guarantee complete long term operation tightness?
Valves have been located and welded as per recommended manufacturer procedure.
We openened 1 valve, found no particles in it preventing tightness. Representative replaced internal parts but it did not solve the problem.
If you need more info please tell me.
Regards,
We recently installed a piping network in which there are several gate valves.
All gate valves are socket welded, 1500#, SA-105, metal seats, less than 2'.
Fabricated and tester as per ASME B16.34 @ API-598.
Operating conditions: 1500psi@520F
A few valves have shown some leaks during operation. My customer told that those leaks are not acceptable and asks for perfect tighness of all valves.
My question for you guys are the following.
-Are my customer request realistic?
-If it is not realistic, is there official documentation stating maximum leakage during operation?
API-598 & ASME-B16.34 indicates zero leakage during testing for those diameters, but it is only for 15 seconds, at cold temperature. Does those tests guarantee complete long term operation tightness?
Valves have been located and welded as per recommended manufacturer procedure.
We openened 1 valve, found no particles in it preventing tightness. Representative replaced internal parts but it did not solve the problem.
If you need more info please tell me.
Regards,





RE: Gate valve tightness issues
The main thing to consider is if it really matters or not. If the resulting leakage rate is so small that it takes hours, days, weeks, or months to fill the volume of the pipe downstream, does it matter?
Ultimately, the method of leak testing and the equivalent leak rate (for example, 1 bubble every 16 seconds)needs to be carefully considered and selected so it is appropriate for the system use. If a water system for your lawn, who cares. If toxic or even lethal gas, then leakage is really important and should be checked much more carefully.
RE: Gate valve tightness issues
However, even if leaks can be tolerated, my customer will not accept any unless I prove the actual leak rate is acceptable. I'm looking for a reference standard quantifying acceptable leak rated during normal operation over extended period of time, or at least stating that some leaks are inherent during operation. If leaks are too high, so be it we will replace it. If it is normal, and any gate valve will shown similar behavior, then it's different.
Maybe you or someone know about this kind of documentation, because so far, I have found nothing about it.
Thank you
RE: Gate valve tightness issues
i hope the standard EN ISO 15848-1, section 6, whcih talks about tightness classes would answer to your question,.
RE: Gate valve tightness issues
RE: Gate valve tightness issues
Once you find this out, then test the valve per the requirements of the standard (media, pressure, and time). If the valve passes, then the customer has no right to question unless they specifically ordered something else.
Please note that ASME B16.34, as mentioned in a message above, does have test methods for valves, but it does not have acceptance criteria. So this standard will not help you other than to define a commonly used test procedure.
RE: Gate valve tightness issues
And if you want nominal "perfect tightness", it should be double block and bleed with soft seated valves.
RE: Gate valve tightness issues
Clearly, any piece of equipment being tested either passes or fails the test.
In my history within the operating world, however, I am accustomed to stating that when a valve "passes" it is allowing the controlled medium to "pass" from one side of the valve to the other WITHOUT escape of medium to the environment or ingress of air or other contaminant/adulterant into the controlled system.
When a valve "leaks" however it IS allowing escape of controlled medium to the environment [or ingress of...as stated above].
Hope this helps.
CR