Looking at the RUS distribution standards for double circuits (For example VD1.81) it appears to show a single neutral. Am I reading this correctly?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Double circuit distribution neutral
|
RE: Double circuit distribution neutral
RE: Double circuit distribution neutral
1) all poles are grd to the neutral. non device poles use a grd plate @bottom of the pole and device poles use a grd rod.
2) most 3ph xfmr banks primaries are delta. most wye 3ph banks prim. with a ungrd neutral and the rest use grd N.
3) 1 ph use the grd N and also surge arrestors, gang sw, both primary and secondary metering use grd N.
It is a little different but it will work. I would also believe the 2 - 3ph 4w circuits come of the same buss with separate oc devices ( bkr, reclosers ect.
Hope this helps and good luck
Dave