Double circuit distribution neutral

Double circuit distribution neutral

Double circuit distribution neutral

(OP)
Looking at the RUS distribution standards for double circuits (For example VD1.81) it appears to show a single neutral. Am I reading this correctly?

RE: Double circuit distribution neutral

Why would you expect more than one neutral? It only carries unbalance current; the better the distribution planner/designer/engineer does, the less the current. Certainly two circuits worth of unbalance won't overload one conductor. Both circuits having a fault to ground on the same phase at the same time might be an issue, but the odds of that happening are diminishingly small.

RE: Double circuit distribution neutral

Mudcat, youn are correct, 2 circuits of wye 3 ph 4 wire 24.9/14.4 kV sharing the same neutral. The same is true 12.47/7.2 kV. I looked up sections of G (Transformer connections) and H (Grounding)to verify their reasoning.
1) all poles are grd to the neutral. non device poles use a grd plate @bottom of the pole and device poles use a grd rod.
2) most 3ph xfmr banks primaries are delta. most wye 3ph banks prim. with a ungrd neutral and the rest use grd N.
3) 1 ph use the grd N and also surge arrestors, gang sw, both primary and secondary metering use grd N.
It is a little different but it will work. I would also believe the 2 - 3ph 4w circuits come of the same buss with separate oc devices ( bkr, reclosers ect.
Hope this helps and good luck
Dave

RE: Double circuit distribution neutral

(OP)
Thanks for the information. I didn't think that the current would be an issue but wasn't sure about relaying.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources