Trip curve for FPE NEF421050 breaker?

Trip curve for FPE NEF421050 breaker?

Trip curve for FPE NEF421050 breaker?

(OP)
Good afternoon.

I have been asked to compile information for an arc-flash survey. One specific request is giving me some trouble. I need to find a trip curve for a 50A federal pioneer electric breaker, cat #NEF421050. This is on a 129vdc system. I am aware of the history of FPE breakers and understand that these trip curves may or may not be relevant for real life applications, but we still require the data to run the calculations.

Any information would be greatly appreciated.

Thank you very much.

RE: Trip curve for FPE NEF421050 breaker?

low1

I have nothing in my files about that FPE breaker. Try a website Widespread Electrical Sales, they have your breaker in question. Enter the part # and some of the spec's are shown. A note below request for a "cut sheet" that might be the trip curves.
I don't like FPE breakers period. I saw a 34 year old electrician loose his right hand and his face burned badly. All he did was turn off a 60 amp MCCB, with no load on it. The cause was never indentifiled. FPE tried like hell to say it was his fault in court. I was on the witness stand just before noon recess. During the recess I was paged by my office. There was 2 other same breakers exploded the week before. FPE still said it was his fault, the jury rewarded him $7.2 million plus all his employer Workman's Comp for all past and future Medical bills. That was in 1984.
The 129vdc sounds battery voltage for swgr. The MCCB is rated 14kA @ 480v I do not know if is rated the DC, bet it isn't.
Good luck.

RE: Trip curve for FPE NEF421050 breaker?

(OP)
Thank you very much, greatly appreciated. That's exactly what I need.

Melspuds, I understand and completely agree. Thank you for the insight.

RE: Trip curve for FPE NEF421050 breaker?

I know some of the FPE stab lok residential breakers had issues but never heard of any issue with industrial breakers, we test them all the time and have not seen any higher failure rates than any other brand/line. In fact there are much worse.

Anyways, here is the curve. This is for Federal Pacific NEF, I didn't know Federal pioneer had a NEF?

RE: Trip curve for FPE NEF421050 breaker?

(OP)
Yes, pacific. My mistake :)

Thank you very much everyone!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources