We are designing a residential building in a heavy snow area. The maximum load on the roof (snow+drift+dead) is about 150 psf. Per the IBC, tables 2304.7(3) and 2304.7(4) the maximum load I see is 100 psf (table 2304.7(3)) for 3/4" sheathing.
Is plywood not possible for the loads?

I am attaching an APA rated span and load table 1b (page 3) that shows that if we use structural I sheathing with a 48/24 rating (thickness of 23/32, 3/4" or 7/8" per the IBC tables) we have capacities of 469 psf and 285 psf in bending (3 span condition) for strength axis perpendicular and parallel to supports for trusses at 16" o.c. If I reduce them down per adjustment table 5 in the attachment to a 1 span condition, the loads are still below our required loads. Is it ok to use these tables?

Another question, I have is regarding the fasteners for 3/4" sheathing for diaphragm capacity. The IBC does not have any tables for 3/4" sheathing. Is there a particular fastener that is used in these conditions? What tables/design do I need to follow to account for the 3/4" sheathing.

RE: Plywood Structural Sheathing at Roof in High Snow Area

Two layers gets you double the capacity. More labor and cost there but that is an option - perhaps (2) 5/8" layers?

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Plywood Structural Sheathing at Roof in High Snow Area

If you need the 3/4" ply for gravity loads but the numbers for 5/8" ply work for lateral then I would just provide the nailing spec for the 5/8" and be done with it.

RE: Plywood Structural Sheathing at Roof in High Snow Area

When using JAE's alternative, don't forget to increase the fastener length on the second layer. Theoretically not necessary, but adds to capacity and doesn't cost a bunch.

RE: Plywood Structural Sheathing at Roof in High Snow Area

I'd suggest that you contact the APA-EWS American Plywood Association help desk. They routinely coordinate with the building code people. They will be able to give you an exact answer on both questions. They are quite helpful. Almost certainly you can use the tables referenced in your case and they can discuss the nailing question at length.

RE: Plywood Structural Sheathing at Roof in High Snow Area

be careful assuming you will get a 3 span or even a 2 span condition in the field

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources