We have an acs800 drive. We also have a hand/off/auto switch. My question is how do we wire this HOA switch into the drive to give a manual start when we also have an auto start going into the drive?
Thanks
Thanks





RE: Wiring of a vsd
If you are sending 12Vdc to the drive from the automatic control tie a fixed 12Vdc to the other terminal of the HOA so that is sent via the HOA if set to Hand. Likewise 24Vdc if that's what the automatic controller is sending.
So, the HOA's common terminal is going to the drive and one of the other terminals goes to the automatic controller and the last goes to a fixed voltage. One position hooks the automatic signal to the drive, a second position interrupts the all signals to the drive, and the third position sends the fixed voltage to the drive.
Keith Cress
kcress - http://www.flaminsystems.com
RE: Wiring of a vsd
There are quite a few options and you haven't given us any facts.
Study the manual or get someone do it for you. It is a little more complicated than a three-way switch for a lamp.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Wiring of a vsd
RE: Wiring of a vsd
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Wiring of a vsd
When we turn the switch to hand. Do we wire the start push button in series with the hand contact?
Thanks
RE: Wiring of a vsd
Chuck
RE: Wiring of a vsd
Without knowing for sure, the GENERAL methodology in drives programming is that you program one of the digital inputs for Start/Run (assuming 2 wire control), hard wired to the Hand position of your HOA switch as the Local command. Then program another input as "Local-Remote", hard wired to the Auto position of your HOA switch. Then, as an example depending on how THAT drive says it reacts, when the L-R input is low (off), the drive does nothing unless the Start/Run command goes high. When the L-R input is high, the drive is on Remote Control and accepts whatever is supposed to control it automatically, such as the communications port from a PLC, and also ignores the Start/Run input terminal status. If your remote control is via digital inputs as well, then you have to set up another input as the PLC Start/Run command. But again, all of this is very very specific to how THAT drive functions.
If you would like me to RTFM and program it for you, please forward $100,000 US to my PayPal account immediately, that will cover my time and whatever travel costs it will take to get me to your drive, wherever you are. There are others here who would likely do it for less, but they are not me...
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: Wiring of a vsd
I could contemplate a somewhat lower fee, though.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Wiring of a vsd
Lc85,
Hire Skogsgurra, he's better than me anyway and you can probably get him for less.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: Wiring of a vsd
I DO NOT WANT THAT KIND OF JOBS
That is something that any sparky that can read a manual can do.