Lets say I have a switchboard that requires ONLY 3 Phase loads, transformer, UPS, Motors, ETC. ( no neutral is required at all)
Now lets say I am feeding this from a generator where I have 4 wires from the alternator ABCN connected to the aforementioned switchboard.
the N of the generator alternator is Bonded to ground inside of the aforementioned switchboard but NOT at the generator location.

The 3 phase loads that are feeding from the switchboard are non-linear and have a fairly "dirty" harmonic profile.

The question is will i see any harmonic loads on the neutral conductor between the main service and the generator?

can someone point me to a white paper or other documentation that clarifies this point either way?

thank you

-Deepro





RE: Harmonics on neutral ?

Yes. The generator will produce some harmonics all on its own. There may also be some coupling between the phase conductors and the neutral.

RE: Harmonics on neutral ?

(OP)
let take the generator and capacitance coupling the the equation.

The question is will i see any harmonic loads on the neutral conductor between the main service and the generator?

can someone point me to a white paper or other documentation that clarifies this point either way?



When an elephant is in trouble even a frog will kick him.

RE: Harmonics on neutral ?

Quote:

will i see any harmonic loads on the neutral conductor

Negligible. By 'harmonic loads' I assume you mean current harmonics. Other than its bonding to ground, the generator neutral is open circuited as none of the loads are connected to it and cannot return their harmonic currents to the source through it.

There may be some capacitive coupling, as David suggested, between phase and neutral. But this impedance is quite high and the resulting currents will be low. And not trivial to calculate, given the unknowns in cable layout, capacitance, harmonic voltages generated by load and generator and their internal impedances to these harmonics.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources