bottom reinforcement anchorage3 into support
Good day,
Regarding the anchorage of positive moment reinforcement, aci318-11 states that u need to enter the support by 150mm and the bar diameter should be small in order to satisfy an equation ( section 12.11.3) (ld <Mn/Vu + la). This option is disregarded if the reinforcement is anchored with a standard hook beyond the center of the support.
Do u usually satisfy that condition or do u just anchor the bottom reinforcement using a standard hook ?
Same thing applies for the 2-way slabs.
in columns strips, bottom reinforcement should be anchored by a standard hook at the slab edge while in the middle strips, 150mm is enough. I think it is too complicated to be done and to verify on site so i ask for all the bottom reinforcement to be anchored by a standard hook.
what do u think ?
what do u think ?
RE: bottom reinforcement anchorage3 into support
Chapter 7 has additional requirements for SOME of the bottom bars depending on certain factors (continuity bars). For those continuity bars I do hook them all in the end spans.
Otherwise I usually go with the 6" (150mm).
As soon as the negative moment pushes the point of inflection a foot or two into the span, the support check becomes irrelevant and the requirement only needs to be satisfied at the point of inflection which is generally easy to do.
In my mind, there's little sense compromising constuctability to quickly tension develop support bars that are in compression. I suppose that one could argue that the designer's detailing ought to be consistent with their analysis assumptions at faux pins. That's a whole separate kettle of fish however.
However, if your support has a small width and the top reinforcement can not be anchored since it wont be developed, then your support will be fully pinned.
I think there are some topics in the code which results in congested reinforcement areas but when u the client has hired a sub consultant, you are obliged to satisfy the code requirements.
For example, regarding the 2 way slab, any ideas why the top reinforcement extension should have a length equal the third of the biggest span from each side and not rely on the FEM method even if it results in smaller bars extensions.
Correct. As far as I'm concerned, any proper design is going to include top steel over the supports.
Sure, if your case is one of the rare, truly pinned supports, then the bottom steel anchorage checks at the support would apply. The overwhelming majority of the one and two way CIP slabs that I deal with are monolithically connected to CIP beams, walls, or columns. The only exceptions that come to mind are the odd case where slab end spans are supported on steel or masonry, mostly in renovation applications.
Yes, we are always required to satisfy code requirements. My point is that the code requirements regarding positive steel anchorage at supports do not apply to the vast majority of supports. This is true, at least, in my practice.
As luck would have it, I now exactly why this is the case:
1) Designer sanity. Making every run of bars it's exact FEM required length is tedious.
2) Engineering judgment. FEM results are an answer not the answer.
3) Constructability. Assembling and inspecting a slab where every run of bars is different is difficult and error prone.
That said, unsymmetrical top bar mats are a QC nightmare. They will occasionally be installed backwards or symmetrically. In the situation that you've described, there may well be top steel demand over the entire 6m span. This is particularly true when unbalanced live load is a consideration. A practical top mat may well be a symmetrical one that spans over the entire 6 m span.
What i usually do is to take these bar extensions as a minimum and check using the finite element method that the required reinforcement falls within the required range and if not, if would increase my bar length.
I would be grateful if u could indicate where did u find the clause saying that the bar extensions need not to be followed unless we are designing the slab the Direct Design Method .
thank u
No. I dug around and came to the conclusion that I've been wrong about this. ACI figure 13.3.8 needs to be adhered to for all methods it seems. Good thing that's what I do.
Me too.
I see that u are very active Mr kootk. Very good job and answers ! keep it up ! cheers