Allowable crane traction frame drift?

Allowable crane traction frame drift?

Allowable crane traction frame drift?

(OP)
I have a building I designed to accommodate a 15ton pendant operated bridge crane. The project ran over budget and the client decided to reduce the size of his building. Unfortunately the portion of the building he decided to eliminate contained a brace used to resist traction forces of the crane. I am now being asked to design a frame that will allow the space under the crane to be open (a moment frame). So I am wondering what the allowable drift of this frame should be?

I am considering using H/400 but I am not sure if this is even correct. All of the literature I have relates to deflection of the crane girder and drift of the building perpendicular to the crane runway but I have yet to come across anything that gives this limit.

RE: Allowable crane traction frame drift?

Try the MBMA Design Manual and look in the crane section for longitudinal crane loading. H/400 seems excessively stiff unless the crane is supported on masonry columns.

Jim H

RE: Allowable crane traction frame drift?

(OP)
I used to have one of those manuals.... but not anymore.

RE: Allowable crane traction frame drift?

AISC Design Guide 3, second edition (Serviceability Design Considerations for Steel Buildings) gives some treatment to this topic. Refer to Chapter 7 and the Appendix.

RE: Allowable crane traction frame drift?

Crane's are very dependent on minimal deflection. CISC has a great (free) design guide for steel structures supporting cranes. The CMAA also has an $84 specification (I think #70 or 74) for bridge crane requirements.

I believe H/400 is the right number.

RE: Allowable crane traction frame drift?

(OP)
I have the first edition of DG 3 and I never would have thought to look in there. I was looking in DG 7. So It appears as if H/100 is allowed..... but I think I am going to be slightly more strict than that.... especially since they said movement of the frames could be observed during operation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources