Glycerin antifreeze systems

Glycerin antifreeze systems

Glycerin antifreeze systems

(OP)
Hi, have a question regarding some antifreeze systems i service. The systems were designed about 10 years ago and have appx. 560 gallons of Glycerin premix in them, and were installed with expansion piping instead of tanks. The worst of them has 3 10" pipes about 8' tall, which have been next to useless when the temperature goes up in the attic of the facility. I can drain the expansion pipes repeatedly, but the air keeps bleeding into the system after a few months.

I prefer to use bladder tanks in systems, but my customer is "thrifty" and seems to think that pressure increasing to over 180# is ok. They had a pressure relief valve that kept pissing all of the glycerin down the drain....then diluting the mix when it cooled down. My main question is, what is the opinion out there of using these air-charged pipes instead of bladder tanks?

Also, am looking for places to recycle diluted Glycerin premix in Ohio because i figure the EPA would frown upon dumping it down the drain.

Thanks for any help and advice. Chris.

RE: Glycerin antifreeze systems

I don't have a suggestion for the expansion piping, but I can suggest Safety Kleen for glycerin and/or propylene glycol recycling. They charge approx $18 per gallon, so you have to add that into your pricing when recharging an antifreeze loop.

Randy

RE: Glycerin antifreeze systems

NFPA 13-2013 Section 7.6 covers antifreeze systems. The Automatic Sprinkler Handbook has commentaries as to why and how to install antifreeze systems. NFPA 25-2014 has commentaries about servicing and maintaining antifreeze systems. I do not know about expansion piping, but listed expansion tanks are required on newer antifreeze systems.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources