Effect of frost on sheet pile wall in saturated clay
(OP)
Hello,
I'd like to hear your opinion on the effect of frost on a sheet pile wall (internaly braced) in saturated clay. Should the soil pressure be multiplied by a factor (like 50%)?
Any of you have experiences of such case that you could share?
Thank you very much,
Jonathan
I'd like to hear your opinion on the effect of frost on a sheet pile wall (internaly braced) in saturated clay. Should the soil pressure be multiplied by a factor (like 50%)?
Any of you have experiences of such case that you could share?
Thank you very much,
Jonathan





RE: Effect of frost on sheet pile wall in saturated clay
RE: Effect of frost on sheet pile wall in saturated clay
Mike Lambert
RE: Effect of frost on sheet pile wall in saturated clay
I once saw the walls of a reinforced concrete pit under a truck scale bowed inward until they pinched the platform and rendered the scale useless. When the pit was demolished and the surrounding soil excavated, what is described above was evident. This was in northern Iowa. The frost had penetrated laterally about two feet from the wall. Away from the pit, the vertical frost penetration was about three feet.
In another case, the floor of a freezer room in an ice cream plant was heaved about 8 inches over a period of years by ice lenses in fat clay. Even more interesting, when the soil was thawed, the floor settled 16 inches.
I can't guarantee that the wall will be affected, but if the potential consequences are severe, insulating it would be wise.