Checking defl'n on a multi-material beam
I have a funky beam that I have been tasked at checking, it is a 3Ply 1.75" x 14" 2.0E LVL where the contractor went ahead and bolted a steel plate to each side.
The LVL alone can handle moment & shear requirements but doesn't quite cut it for defl'n. I checked the deflection through method of multiple materials by transforming the sections of steel to LVL by:
(Esteel=2x106psi)
(ELVL=29x106psi)
n = Esteel / ELVL
then multiply the thickness of the steel plate (3/8 inch) by the n value to get a modified beam of: 1.75" x 3 + 5.4" x 2 =~ 16" wide, ran deflection and it all checked out.
I haven't done anything like this since mechanics of materials class 10 odd years ago - so just want to make sure!
(Esteel=2x106psi)
(ELVL=29x106psi)
n = Esteel / ELVL
RE: Checking defl'n on a multi-material beam
I normally size steel reinforcement to support the entire load and just have the wood transfer the force into the support.
I was shooting for L/360 and L/ 240 respectively. When taking the steel into account the total deflection was L/480.