development length for tension and conpression bars.

development length for tension and conpression bars.

(OP)
hi,
regarding the development length for a bar in tension, and in order to be able to develop fy, i should anchor it ldh + the standard hooK which is 12db according to aci318.
if my column section is not big enough to ensure the ldh and i dont want to use the reduction factors allowed in the aci, can i simply develop ld into my column and bent the tension bar inside to have a total length of ld.?

2. the development length for a compression bar is the maximum between 20cm and 18 db (plus or minus depending on the f'c of the concrete). if my section isnt big enough, am i obliged to go this 18db straight or can i go down the allowable distance and anchor the remaining length by a hook ?

RE: development length for tension and conpression bars.

Quote:

can i simply develop ld into my column and bent the tension bar inside to have a total length of ld.?

I don't believe that is appropriate to bend a bar and add up the length to get ld.

Either you develop the bar with a straight length ld or you use a standard hook with the ldh.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: development length for tension and conpression bars.

(OP)
Ok. Same thing applies for the compression i assume. Any references ? Does The aci mention that u need to go straight for the ld ?

RE: development length for tension and conpression bars.

Compression needs to be a straight bar, period. Hooks are not effective for development of bars in compression.

RE: development length for tension and conpression bars.

(OP)
Ok. Thats one thing. regarding the tension bara, any reference that u cant develop ld with a hook as stated above ?

RE: development length for tension and conpression bars.

I've been meaning to ask a similar question for a long time. Here's what I know (or think that I know):

1) I agree with Mr. Hershey that there's no hope for the compression bars. Straight development or nothing.

2) Many old school details that I've seen for slab steps etc clearly do make the assumption that bars can be tension developed by having hooks longer than standard hooks.

3) North American codes do not seem to have explicit provisions for developing bars with longer than standard hooks.

4) The eurocodes do seem to have provisions for developing tension bars with hooks longer than standard. The checks centre around calculating the bearing stresses inside the bar bend and specifying the bar bend radius accordingly. My takeaway from this is that a) small bars probably can develop around the hook with standard bend radii and b) large bars usually need to have their bend radii larger than standard to make a go of it.

5) Using the curved bar node concept of the strut and tie method, one can design themselves an extended hook bar development system that would be compliant with North American codes,.





I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: development length for tension and conpression bars.

Here's a link to purchase the article:
Link

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: development length for tension and conpression bars.

A hooked bar may develop ahead of the bend, but one problem with developing the bar before the bend is that the concrete inside the bend can crush. Some hook length research found this to me a limit state which resulted in bar failure due to this crushing so it was considered in determining Ldh.

Another issue is whether the depth of the hook provides adequate restraint. The bar could be developed without having sufficient concrete to fix the connection.

CRSI is currently funding research on hook lengths and diameters. The first project is nearing completion and my understanding is that it has verified that the current hooks are still valid. Another set of research is underway to examine hooks in high strength reinforcement, which were not part of the older code research. The high strength research will be a longer project since higher concrete strengths will need to be examined and the need to evaluate various means of achieving high strength ductile reinforcement.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close