Power Cable & FO Cable in Single Conduit

Power Cable & FO Cable in Single Conduit

Power Cable & FO Cable in Single Conduit

(OP)
Is it allowed to run 220V power cable and Fiber Optic Comminication Cable together in a single conduit ?

RE: Power Cable & FO Cable in Single Conduit

Under which country's regulations?

RE: Power Cable & FO Cable in Single Conduit

(OP)
@ ScottyUK ... As per KSA regulations where NEC and IEC standards are being followed

RE: Power Cable & FO Cable in Single Conduit

Under British regulations I'm not aware of anything which prohibits LV power sharing a duct with optical fibre; it isn't unusual to see this type of installation.
We don't see a lot of conduit in this country, and most of what we have is small diameter (20mm / 25mm) and wouldn't be used for a fibre route.

RE: Power Cable & FO Cable in Single Conduit

(OP)
Thanks ScottyUK..

RE: Power Cable & FO Cable in Single Conduit

(OP)
@ Scotty.... Why 20mm / 25mm dia. conduits aren't used for the FO circuits as what you have mentioned ? I believe these should be OK for smaller cables like F.O 4 core etc.

RE: Power Cable & FO Cable in Single Conduit

21mm is the trade size for 3/4" conduit in the NEC. The minimum bending radius permitted for 3/4" conduit in Chapter 9, Table 2 of the NEC is 4 1/2" or 114mm, so with some fiber cable you might need to use a bender with a larger bend radius. The biggest issue would be conduit fittings which would have a smaller bending radius than what would be permitted for the fiber cable.

770.110(B)(2)indirectly permits non-conductive fiber cables to be installed in the same raceway with power conductors.

RE: Power Cable & FO Cable in Single Conduit

Since it is Fiber Optic, there is no risk of electromagnetic interference. Also, please note that in a 220 kV Over Head Line (OHL), it is common to take the fibers through the OPGW (Optic Fiber + Ground Wire) conductor. These fibers are along with the phase conductors for many miles.

Please don't forget that these fibers are used for critical applications such as substation to substation communication, SCADA, Feeder Differential protection etc. This is a common practice, even in KSA (Kingdom of Saudi Arabia??). By the same token, I do not see any reason, why the same conduit cannot be used, unless there is some abnormal temperature rise issues are the limitation.

RE: Power Cable & FO Cable in Single Conduit

Hi PZC,

To be honest we rarely see conduit used in the UK except for indoor small / medium power installations in factories and commercial premises. The majority of external work and heavy industrial applications use single wire armoured cables. Most fibre I see in the UK is either wire armoured, or kevlar armoured in applications where it's desirable to avoid metallic interconnection of the two locations, because that follows typical British practice. If the fibre in question was non-armoured and it was possible to stay within bending radius constraints then I guess it could be routed through conduit.

krisys - it is true that fibre itself is immune to electro-magnetic interference, but that's not always true of the overall FO cable where metal wire, braid and tape armours are all possible construction variants. Metallic armour can introduce touch and transfer potentials if only one end is earthed, or provide a path for circulating currents if both ends of the armour are earthed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources