Exterior Load Bearing CMU wall with Sill Block Transition Detail
I have a client that wants to use a detail as in the attached sketch for an exposed, exterior load bearing cmu wall. He has a 12" block transitioning to an 8" block with a sill block that is 6" wide (nominal dimensions). He is showing a 6" wide CMU block adjacent to the 6" wide sill block.
It appears as though there is inadequate clearance between the rebar centered in the 8" cmu above and the face shell of the 6" block for grouting.
Has anyone every detailed a cmu wall similar to this? Should the face shell of the 6" cmu block be knocked out to allow clearance for the grout around the rebar?
Thanks!
Thanks!
RE: Exterior Load Bearing CMU wall with Sill Block Transition Detail
For 1) - if you have them grout the lower courses first, prior to settint the 6" block you should be OK
For 2) - the one block with a lack of bond wouldn't create a significant problem in my view.
Grout the 5 courses of 12" conc. blk. Set the sill blk. in a full bed of mortar, and at the same time, cut the inner face off the 6" conc. blk. and set it with the inner face and cross shells bedded in mortar. Then continue the 8" conc. blk. Put horiz. ladder reinforcing in the joints below and above the sill blk. You probably couldn’t high lift grout this wall arrangement in any case.