Fan control
Fan control
We're installing some vent fans in building A and want to be able to control them manually from building B. The control requirements are simply on/off/reverse. The two buildings are about 1km apart. There is a fiber optic communication backbone between both buildings.
After some research, I am thinking of doing the following:
Bill
- Use fan soft starters in Bldg A containing a module that supports MODBUS TCP. Through this fieldbus, it's possible to start and stop the motor, read out currents and frequency, achieve info about warnings, faults, etc.
- Use a desktop PC in bldg B running Wonderware HMI software, which will send MODBUS TCP commands to the softstarters
- Use switches to convert from Ethernet to fiber (bldg B), fiber to Ethernet (bldg A) and then route the signal to individual starters.
- Note: No PLC is used
- Will this work?
- Are there other alternatives I should look at?
- Would I be able to remotely login to the desktop PC to monitor and control the fans from another location if needed?
Bill
RE: Fan control
RE: Fan control
1. We will have local disconnects/hand off autos at the fans for emergency stop
2. I was planning on using just a PC with Wonderware. For redundancy, we will have a spare PC.
3. Re: security, I will check with our IT dept about using an ACL, firewall and/or encryption. Thoughts welcome.
Bill