arcing on 13.7kv transformer inlet

arcing on 13.7kv transformer inlet

arcing on 13.7kv transformer inlet

(OP)
hi guys,
it has been reported to me that on a distribution transformer (750KVA , 13.7 Kv) an arcing had caused the definitive damage of the transformer.




i was wondering if some of you already experienced this kind of problem , and if the caps on the unsused HV inlets are sufficent in term of insulation , as this transformer is in a tropical country (Haïti to be precise).
the local electrical engineer is only focused on a sabotage , because of the hole in the cap , he seem to ignore the effect of high voltage on thin insulation :)
so i would like to have you opinion on that problem , who seems to me to be a insulation defect of the inlet connector and maybe a cap not appropriate for securing the unused inlets.
thanks in advance

best regards

Jean Michel

RE: arcing on 13.7kv transformer inlet

(OP)
Link
Link
Link
Link

pictures of arcing

RE: arcing on 13.7kv transformer inlet

Bushings grade the voltage properly, caps are for keeping the dust out during shipping.

RE: arcing on 13.7kv transformer inlet

Stevenal is right. You need a bushing well plug, not just a plastic cap.
Google bushing well plug and several suppliers come up.

Regards
Marmite

RE: arcing on 13.7kv transformer inlet

Those plastic caps are not sufficient. When you have unused deadfront wells, you should be using a bushing well insulated plug. If you have unused inserts in the wells, you should be using the appropriate insulating cap. Some applications use arrestors instead of the protective caps. As stated above, those caps in your photos are for shipping and storage purposes.

RE: arcing on 13.7kv transformer inlet

(OP)
many thanks guys , do you have some references or regulations for me to study about shipping caps ?
unfortunately , the supplier / installer saw the word "sabotage" and as this sound good to him (cancellation of warranty and supplying us a brand new transformer ) i predict we 'll have a hard time to convince him to repair and correct the installation , at his cost.
thanks again , from Haïti
with my best regards

Jean Michel

RE: arcing on 13.7kv transformer inlet

(OP)
thanks again to all of you , this was very helpful.thumbsup2

Jean Michel

RE: arcing on 13.7kv transformer inlet

(OP)
end of the story : a Dominican company is going to check the transformer (insulation etc.), replace the damaged bushing and put insulations plugs in unused connectors. thanck to ABB and Eminsa .

best regards

Jean Michel

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources