Emergency venting (in case of fire) for pressure pressure vessel
Hi everyone,
I have to calculate flow rates from emergency venting for tank wich looks like to a pressure vessel. The tank is supported by legs. The bottom is an ellipsoidal head and the top is a flat head.
Pmax :100mbar
Vaccum : 30 mbar
Temperature : 135 °C
Which code do i use to get it. I think we can't apply API 2000
Thanks.
RE: Emergency venting (in case of fire) for pressure pressure vessel
Check IFC, NFPA, or AHJ. depends upon the fluid class. i ended up using API 2000 for a tank holding a chemical solution (pool fire case) and the client accepted it. for the pool fire case, i had to demonstrate whether or not the existing tank vents were adequate. ended up recommending using existing blinded connections for the emergency vent case.
good luck!
-pmover
check https://www.fauske.com uder technical papers,..you will found answer there.
Suggest use of the same code as that which was used for the mechanical design of this vessel or tank.