Folks,

I am using a 40A motor contactor to energize a circuit with the following components:

4 motors each rated for 208V, ¾ HP, 5.2 FLA (manufacturer’s info)
1 motor rated for 208 V, 1/3 HP, 2.3 FLA (manufacturer’s info)
and a  total of 14 A non-motor load (mini-fan, ballast, horn, indicating lights, ...)

Isn’t it a misapplication to use a motor contactor to energize non-motor loads?  I am using a Square D contactor SC02 type.  Many thanks for your comments, -Mort

RE: Contactor Type

A quick look at the data sheet (http://164.109.40.74/huggy_pdf/en/SD/8502sec1.pdf) indicates that your contactor is only rated for either 27 or 36 amps, not the 40 amps that you state.  Those lower ratings could be a problem.

Otherwise, it's OK to use a motor contactor for the loads you indicate.  Motors are, generally speaking, a "difficult" load to start due to their inductive nature, compared to other resistive loads such as lights, heaters, etc.  You can use a motor contactor to control resistive loads, but you cannot use a general purpose contactor to start a motor, at least not without proper derating.

Make sure you have provided overload and short circuit protection for all loads per code requirements.  And double check the rating of your contactor as I mentioned above.

RE: Contactor Type

To my way of thinking I would have individual motor starters for each motor or at least a single properly rated contactor with individual overload relays for each motor and a seperate contactor for the non motor load.  That would provide the proper overload protection for the motors.

RE: Contactor Type

P.S. The above installation would also easily facilitate troubleshooting of an overload trip condition.  The tripped motor(s) would be obvious.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources