NEC 250.50 Exception:
"..where the steel reinforcing bars or rods are not accessible for use without disturbing the concrete."
If the Ufer grounding was not well prepared before concrete pouring one has to "disturb" the concrete in order to connect it with the general grounding electrode.
IEEE 665/1993 ch.5.7.4 Station reinforcing steel states:
"When reinforcing steel is connected as part of the ground grid, it should be recognized that there may be some risk of damage to structural concrete for high values of ground current."
That means a large ground fault current flowing through the rebar would heat the steel and the concrete adjacent evaporating the concrete moisture and destroy the concrete.

RE: thread238-193951

For your edification and amusement search mineral accretion, Wolf Hilbertz, and biorock. Your interest is in AC but if you move to DC, concrete can be repaired by mineral accretion or structures even grown from rebar in seawater. A ground rod inserted in concrete does make the best ground.

RE: thread238-193951

(OP)
IEEE is special for Generation Station Grounding, can it be applied to the earth network of a modern data center building?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources