Refering to thread238-193951: Does Grounding Rebar (Ufer) Weaken Concrete? just wanted to add that NEC 250.50 allows attaching concrete base rebars to earth and does not require it.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: thread238-193951
"..where the steel reinforcing bars or rods are not accessible for use without disturbing the concrete."
If the Ufer grounding was not well prepared before concrete pouring one has to "disturb" the concrete in order to connect it with the general grounding electrode.
IEEE 665/1993 ch.5.7.4 Station reinforcing steel states:
"When reinforcing steel is connected as part of the ground grid, it should be recognized that there may be some risk of damage to structural concrete for high values of ground current."
That means a large ground fault current flowing through the rebar would heat the steel and the concrete adjacent evaporating the concrete moisture and destroy the concrete.
RE: thread238-193951
RE: thread238-193951
http://www.wolfhilbertz.com/accretion.html