Trench Footing Placed in Water

Trench Footing Placed in Water

Trench Footing Placed in Water

(OP)
I received pictures from one of our projects showing continuous trench footings being placed in water. The water is half way up the trench, rebar has already been places, and concrete is being placed in the trench as is. Can any one come up with a reference where this would not be allowed or is this common in areas with high water tables. I guess as the concrete is placed, it would push the water down the trench and out and would not mix much, if any, of the mixed concrete with the water in the trench. Any comments on this would be appreciated.

RE: Trench Footing Placed in Water

This is done from what I hear on some bridge pier type jobs however this is not ok.

Especially if the rebar has been sitting in this water for any length of time.

RE: Trench Footing Placed in Water

Quote (Kennyb04)

Is this common in areas with high water tables?
No. A typical method is to pump the water from the excavation with a diaphragm pump (mud hog) then immediately place the concrete before the excavation refills with ground water. Winds up being a "best efforts" technique, but with skill and experience a Contractor can do good job.

Placing concrete directly in standing water will wash out too much cement from the mix, giving unpredictable results.

For larger placements, concrete can be successfully placed under water with a "tremie". Here is a short explanation of the principle: http://en.wikipedia.org/wiki/Tremie
The concrete first placed with a tremie will go directly into water, thereby loosing cement. Once this weakened concrete is in place the tremie works successfully to place remaining concrete "from the bottom up." The initial weakened concrete is compensated for by making the under water structure (say, a cofferdam seal) of greater thickness than theoretically necessary.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: Trench Footing Placed in Water

SRE is exactly right. This will dilute the concrete, increase the water cement ratio, decrease the strength and do so randomly....so you can't predict at any location how much strength you have in the footing. Not good!

This is a bad practice! Do not allow it on your projects. My only change to what SRE noted is that you pump from a sump adjacent to the footing, not in the footing. Pumping from the footing will loosen the footing bearing soils. Pumping from a sump adjacent to the footing will actually tighten the footing bearing soils, if granular material.

RE: Trench Footing Placed in Water

You must have specified a mix or concrete strength required. So get out there and core some footings and run some tests. In the mean time let it be known if tests fail that replacement will be required.

RE: Trench Footing Placed in Water

I agree with above recommendations but must add that footing excavation must also be mucked out (removal of disturbed, soft material) before placement of concrete. As the workers set and tie rebar, walking in the bottom of the excavation may disturb that layer, unless a stone or concrete mud slab was placed in advance. If there is water in the excavation, it can soften the bearing stratum and prevent you from observing whether the excavation is clean or not.

RE: Trench Footing Placed in Water

Can I inquire as to who approved the placement of the concrete in the water? Any contractor and inspector should know that this is unacceptable. To have done it is, in my opinion, very poor judgement. Exceptions can be made - as noted above, but only because all factors were considered and a best approach was made. In this case it is not. Who, now, is responsible for the non-conformance?

RE: Trench Footing Placed in Water

i would bet the inspector is the one who supplied the photos... i'm betting there was discussion or disregarded comments on-site.

RE: Trench Footing Placed in Water

Yeah, I would say the photos are a dead giveaway that someone is telling you something. Time for SuperStructuralEngineer to take charge and do something! K some C's A.

RE: Trench Footing Placed in Water

"This is done from what I hear on some bridge pier type jobs however this is not ok." The way we did these pier jobs over water, was first drive the sheet piles to make coffedams, suck out the river mud and sludge with air lift pumps, pour this concrete mud to the bottom of the flooded cofferdams, pump out the flooded cofferdams after the concrete mud had a chance to harden, then tie up your footing rebar to the steel piles that were driven in water, then pour the spcified concrete for the footing, build more rebar and pour more spec.concrete to build the pier.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources