Control & LV Cable tray in Battery Room
Control & LV Cable tray in Battery Room
(OP)
Does anybody has technical concerns running control and LV cables (208/120) in a open ladder cable tray thought a battery room?
This is a dedicated room for the DC system in utility substation application.
Thanks in advance for the advise
This is a dedicated room for the DC system in utility substation application.
Thanks in advance for the advise






RE: Control & LV Cable tray in Battery Room
However the cable tray and the cables shall be corrosion resistant
If the Battery Room could be considered Class I Division 2 the wiring has to be as per NEC Art.501.(B).
http://www.cwadistrict7.org/Safety-Manual-2012/bat...