Hey what does 2 high mean in terms of breaker arrangement?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
breaker arrangments (2 high, 1 high, etc)
|
RE: breaker arrangments (2 high, 1 high, etc)
RE: breaker arrangments (2 high, 1 high, etc)
The bus will be in the middle, so on the top breaker the feed is from the top poles of breaker. On the bottom breaker it is from the bottom.
This can cause issues with training and labeling the ground and test breaker.
The space savings are obvious. If there is not much racking in / out probably not much an issue. My local utility does not like them for the above reasons.
Consider an electric racking (and lifting) device if you do go 2 high. It makes life easier (and cheaper) for the maintenance.
I haven't heard anything one way or the other, but I suppose if you had a catastrophic failure in a lower breaker, the upper one would suffer (presumably) damage as well.