structural slab on grade design
Hello -
I am in the midst of designing a structural slab floor for a garage/studio area of a single family home. The builder decided that he does not want to compact the soil under the slab so I am designing it as a one way slab with walls supporting the exterior edges and two interior 'beams' of wall on footings. This is a 26' x 28' area. I have calculated the maximum positive and negative moments at the interior and exterior supports and determined the required min. reinforcement. The longest span for the 1' wide strips is 9'-3" so my plan is for a 6" t. slab. I was thinking that I would be placing the reinforcement at the tension sides of the slab depending on the location in the strip (at the supports or in the middle of the strip, top, bottom respectively) however for concrete cast against the earth, min. cover is 3". this means that all my reinforcement is going to be in the center of the slab. I may be over thinking things and I also do not design structural slabs every day so I am wondering if I take the top of the slab as not against the earth and use only 3/4" cover for the rebar at the supports that I wanted to place close to the top or if it really doesn't make a difference for the loads it will experience if all the reinforcement is towards the middle. it is only 6" thick so the distance between the tension and compression faces is not great but I thought I would look for some feedback on this.
thank you
thank you
RE: structural slab on grade design
You may need a thicker slab, or to pour against another surface.
DaveAtkins
Your proposed design sounds like there must be more than just that "the contractor does not want to compact the base"...it sounds like there is poor soil.
Why would anyone go to so much expense and trouble as what you are doing, if it were not necessary? My advice is to retain an experienced geotechnical engineer to advise you. Yes he/she will charge, but his/her advice will save your client a lot of money and keep both you and your client out of trouble, and allow you to sleep at night.
You aren't doing your client any favour by skipping the geotechinical engineer. I have been called in to look at calamities that came about because some inexperienced person missed having the geotechnical engineer on board where soil conditions were not good.
Remember -- your client won't thank you if things go wrong -- rather he/she will sue you. I am a structural engineer, not a geotechnical engineer, but I know their value.
