Causes of humming sound in a transmission line (below 220 KV) other than corona effect

Causes of humming sound in a transmission line (below 220 KV) other than corona effect

Causes of humming sound in a transmission line (below 220 KV) other than corona effect

(OP)
A humming sound (louder, not normal, & as if house-hold meter abnormal sound) heard near one of the 132 kV Transmission line tower, after its operation since 6 years. The transmission line Conductor used is Cardinall with Current Load - max 70 MW. The louder humming sound seems increased from past week, disturbing the nearby resident.

The other arm of the tower hold the other circuit (recently stringed) and currently not energised.

I suppose the effect is not a corona, please suggest what might be the alarming situation to the Power supply system and to the residents nearyby ?

RE: Causes of humming sound in a transmission line (below 220 KV) other than corona effect

If it is not corona it might be some mechanical vibration around 60Hz

RE: Causes of humming sound in a transmission line (below 220 KV) other than corona effect

I think that the answer is in the question; you added that other circuit. Somehow there is now a resonant tuning that didn't exist before. Is the sound at, or a harmonic of, the power system frequency, or is the frequency unrelated to the power system? The new line could be just right (wrong?) to become an aeolian harp. Dampers or a different line tension may be required.

RE: Causes of humming sound in a transmission line (below 220 KV) other than corona effect

Adding another circuit could also have worsened electric field and thus corona. The new circuit is currently grounded? Have you tried to unground it (or vice versa to ground it, if it is currenty grounded)?

Si duri puer ingeni videtur,
preconem facias vel architectum.

RE: Causes of humming sound in a transmission line (below 220 KV) other than corona effect

Sorry, I've realized only now that the voltage level is "only" 132 kV and not 220 kV. At this voltage level corona should not be an issue: most probably the problem is related to aeolian vibrations as davidbeach said.

Si duri puer ingeni videtur,
preconem facias vel architectum.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources