Hi All,
What are typical values of fault levels for generators with respect to their ratings? Also could someone explain what is meant by saturated and unsaturated conditions.
Many thanks in advance

Paul

RE: Generator Fault Levels

The main quantity you're looking for is the subtransient reactance(x''d), which isn't necessarily tied to size.  A typical value is .15, but it's best to get this quantity from the gen. manufacturer.  To find the amount of fault current a gen. can deliver, take the FLA of the gen., and divide that by x''d.

Mike

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources