synchronize parallel generator
synchronize parallel generator
(OP)
Dear experts
I want to configure new alternative power for electrical power system. You can look the system in image attachment.
this picture:

The condition is GTG and STG2 synchronize with system integration 33kV.
I want to ask about the synchronize fedeer to feeder in breaker point A. Is the system eligible for synchronous?
. Or any additional prosedure for synchronous breaker point A.
Please help me to give some explanation. Any comments is really appreciated. Thank you.
Best Regards,
I want to configure new alternative power for electrical power system. You can look the system in image attachment.
this picture:

The condition is GTG and STG2 synchronize with system integration 33kV.
I want to ask about the synchronize fedeer to feeder in breaker point A. Is the system eligible for synchronous?
. Or any additional prosedure for synchronous breaker point A.
Please help me to give some explanation. Any comments is really appreciated. Thank you.
Best Regards,






RE: synchronize parallel generator
RE: synchronize parallel generator
thank you for reply
In this case i want to transfer the power flow from GTG to STG 2 without power off at the load. Is possible if i configure this system with synchronize at breaker point A? or any procedure to transfer the load with switch off the syncronize of GTG/STG2 or 33/11 kV transformers.
Any comments is really appreciated. Thank you.
Best Regards,
RE: synchronize parallel generator
as i could understand that you want to shift load from GTG to STG2.
i want to know that,
are you thinking of Switchoff the GTG during low load hours?
Regards,
RE: synchronize parallel generator
Shift load from GTG to STG2 because a maintenance schedule for bus 11kV and GTG. Bus 11kV at GTG must be power off but keep the load still power on.
Regards,
RE: synchronize parallel generator
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: synchronize parallel generator
But possibility to synchronize breaker point A that condition is both GTG & STG already synchrone with integration system 33kV.
It's possible? specifically in phase angle fedeer to feeder breaker point A. thanks
RE: synchronize parallel generator