One anchorage connection but multiple anchor groups?

One anchorage connection but multiple anchor groups?

One anchorage connection but multiple anchor groups?

(OP)
Appendix D has definition of "Anchor Group" and uses words such as "group of anchors" and "multiple ~ anchors with <some condition>".
I am trying to understand how to identify anchors for above mentioned words for various capacity checking (breakout, blowout, etc.). Here are some of my understand and would like to ask for your input - am I correct? What's wrong? Thanks...

1. in our design practice, for an anchorage design, all anchors are one "Anchor Group", for example, all anchors in one column base connection. So if the checking is for "Anchor Group", it is just ONE checking for one loading case.

2. Both "group of anchors" and "multiple ~ anchors with <some condition>" are referring to a subgroup of anchors of the "Anchor Group". So for each loading case, in all directions (shear and perpendicular components for all edges), the "group of anchors" and "multiple ~ anchors with <some condition>" need to be identified first and then perform corresponding checking.

For example, a line of anchors subject to shear to one edge. Assuming the distances between the line of anchors varies but they are a "Anchor Group" and subject to one result force which distributed to each anchor. I am thinking there is possibility that the "Anchor Group" has sufficient shear capacity. However, the first one, two, or three anchors near the edge and forms a "group of anchors" and the "group of anchors" would not have sufficient shear capacity. If this is the case, the checking needs to check all combinations of "group of anchors" and "multiple ~ anchors with <some condition>". That is lots of work.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources