What drives SCC in Caustic solutions at 150F? High pH or Chlorides?
We are looking to replace a 50% Caustic line. Our pipe spec references NACE and says to use PWHT Carbon Steel up to about 170F. We shouldn't get higher than 150F but it gets hot in Texas and the caustic is not always flowing in the pipe. I've read conflicting reports that 150F may be too high for carbon steel and 50% caustic. I'd like to move to 304L SS but the chlorides worry me. Our upper limit for NaCl in our caustic is 1.3%. There is no telling what our environmental chloride situation is but the line will be insulated so it shouldn't be a huge problem. The Chlorine Institute calls for 304L for this temp/concentration range but there is no mention of chlorides in there.
Is 1.3% NaCl enough to cause Chloride SCC in a 50% Caustic solution?
Should I be looking at a Duplex instead (2205?)? I'd rather not get into the high nickel alloys if I can avoid it because in reality the fluid should never get hot enough to warrant those.
Thanks.
Thanks.
RE: What drives SCC in Caustic solutions at 150F? High pH or Chlorides?
Good on you for realizing that there's a LOT of chloride in modern membrane-cell caustic- a lot of people don't realize that. I didn't, until I had a failure which was likely caused by that chloride!
If the caustic is not being used at a continuous process temperature of 170 F, it sounds like you're within the NACE suggested limits. As long as your process need for the caustic can tolerate a little iron in it, and also presuming that the solution isn't continuously aerated, you're probably OK with your PWHT carbon steel with an adequate corrosion allowance based on the literature you've reviewed- I have no practical experience to contradict it.
As to chloride SCC in stainless steels, high pH alone does not suppress it as far as I know, nor is the high pH alone to worry austenitic stainless steels in the absence of chloride as far as I can remember- I'm away from my references to check. I do have a dusty recollection of a risk of non-chloride caustic embrittlement in stainless steels, which is probably why NACE is recommending PWHT.
For chloride SCC in austenitic SS you only need the following conditions: stress (which can be residual stress from forming or welding etc. or continuous stress from internal pressure etc., so you can usually assume it's always there in some part of any piping system!), chloride above some threshold which varies with alloy and temperature (at 170 F, 1.3% as NaCl is PLENTY high enough), something to accept the corrosion-generated electrons (oxygen typically, but not limited to oxygen), water, and time. When considering Cl concentration, any process which may form concentrated localized brines via intermittent exposure and subsequent evaporation of the water, is particularly dangerous- salt spray falling on insulation being the classic example. Since I understand that chloride SCC cracks generally initiate at pits, conditions which enhance pitting will also enhance SCC risk: acidic pH, low velocity, deposits or crevices, poor surface condition (embedded iron, interrupted passive layer) etc.
If the service is high pressure, I'd stay away from 304 or any other austenitic. That's just a gut feel based on the above reasoning, and again I don't have my refs nearby to check. Others should chime in and contradict if I'm off base on that.
It sounds like the 3XX series stainless it out of the running. The pressure is low enough but chlorides aren't something we really care about as far as the product goes so I wouldn't be surprised if a batch of high salt Caustic was accepted, anything for a discount. We don't mind iron in the product so it looks like PWHT carbon steel might just be our best bet as long as we can control the temperature correctly.
Can you point me to any good resources that deal with this? I've looked at some publishings but most seem to deal with very specific cases and don't make any general statements (i.e. Chlorides over XX PPM will always crack austenitic steels). Are there any good textbooks that deal with general metal corrosion topics? My understanding of corrosion and materials selection is admittedly limited and these things are starting to pop up more frequently.
Thanks!
Do a search here- I've populated my own records with numerous excellent references gleaned from Eng-Tips users over the years, but most of them are on paper rather than saved as .pdfs or as a link list. I also have a couple good textbooks, C.P. Dillon's book in particular and one by Jones if I recall correctly. Nickel Development Institute publications are also top-notch. API 571 has a concise and accurate but brief section about chloride SCC.
I'm hoping that somebody with actual years-worth of service experience with hot 50% caustic will chime in because like reduced oxygen concentration, increased pH has a tendency to suppress SCC to some degree. I don't have the direct experience you're looking for- we always used caustic at or near ambient and only heat traced it to keep it from freezing, and under those conditions 316SS (tubing) seemed to have an acceptable service life. Whether welds or HAZ would eventually crack or not is a different matter.
Thomas J. Walz
Carbide Processors, Inc.
www.carbideprocessors.com
Good engineering starts with a Grainger Catalog.
For piping I would look at using a duplex, perhaps even a lean duplex (2101, 2102, 2201).
They have usable CSCC resistance, and better pitting resistance than 316L.
They also have very little reduction in corrosion resistance at welds.
The real problem with 304 is that if this line was ever flushed with water and the pH dropped all hell would break loose (literally).
Steve Jones
Corrosion Management Consultant
http://www.linkedin.com/pub/8/83b/b04
All answers are personal opinions only and are in no way connected with any employer.
Every failure that I have seen in caustic was NOT caustic cracking, something else happened faster