Converting ungrounded system into High resistance grounded system- Does size of the system matters?

Converting ungrounded system into High resistance grounded system- Does size of the system matters?

Converting ungrounded system into High resistance grounded system- Does size of the system matters?

(OP)
I got a 500KVA, Delta/Star transformer supplying a 3 phase 3 wire heater load in our chemical process plant which suffered recurring failures. Per observations of failure mode - it seemed to be a result of transient high voltage typical of ungrounded system.

With measured system charging current to only 0.37Amp, required neutral resistance is calculated to 561.75Ohm (=360/SQRT(3)/0.37A). To me, 600Ohm, 150Watt resistance should serve the purpose, at least theoretically ?! Or is this a too small a system to go HRG way.

I have no previous experience of such conversion and seeking second opinion.

RE: Converting ungrounded system into High resistance grounded system- Does size of the system matters?

You went the wrong direction in your resistor selection. 550 or probably better 500 ohms would be a better choice. 500 kVA seems on the small side. On the other hand I wouldn't go below 5-10A in the sizing. At that point you have a chance of tracking down a ground fault; I doubt that a 0.37 amp ground fault could be found.

RE: Converting ungrounded system into High resistance grounded system- Does size of the system matters?

(OP)
Thanks davidbeach,
You are absolutely correct in pointing out to choose the lower value of resistance to exceed Ic by Ir as a basis for designing HRG.

Next, I was planning to connect voltage relay (#59) rated 110V to sense the ground fault. The system is pretty simple with only one load equipment to look into for locating the fault and therefore no pulsing control etc may be required. Am I missing somthing?

Thanks in advance!!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources