Does anyone know if the SLG fault that is calculated in SKM translates to 3I0?

RE: SKM SLG

Well I would assume so, as 3I0 is by definition the Phase to ground fault current. SKM however does some convoluted matrix manipulations to acquire the fault values so it will not be exactly that.

RE: SKM SLG

The total fault current will be 3I0, but contributions from individual sources may have the phase current different from 3I0. For instance, the contribution from a grd wye - delta transformer, with the grd wye side connected to the faulted system and no source on the delta side, would have 1I0 in each phase and 3I0 in the neutral.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources