Maximum distance between expasnion joints i open aur above grade parking structure

Maximum distance between expasnion joints i open aur above grade parking structure

Maximum distance between expasnion joints i open aur above grade parking structure

(OP)
What is the maximum distance between expansion joints (or from an expansion joint to the end of the structure) that structural engineers are using these days, for above grade open-air single story parking structures of cast-in-place reinforced concrete? The joint seal must accommodate both thermal and concrete shrinkage movements. "Pour strips" that are placed some time after the adjacent concrete can help the shrinkage issue, but only to a limited extent, since at 28 days only about 30% of the long term shrinkage will have occurred, and anyway contractors do not want to leave pour strips open more than 7 days. Pour strips of course do not help at all with thermal movements.

RE: Maximum distance between expasnion joints i open aur above grade parking structure

An alternative to pour strips are these temporary "lockable" shear connectors from Anchon: Link

They can be left "open" for in-plane movements whilst still supporting vertical loads. They are "locked" based upon construction durations/schedules.

RE: Maximum distance between expasnion joints i open aur above grade parking structure

I was involved with a 260m long post-tensioned concrete multi-storey carpark that had 2 expansion joints (roughly 85m between joints) and a 1.5m pour strip in the middle of each panel. The pour strips were placed 60 days after the slabs were stressed.

That's PT which would have had a greater shrinkage component than RC. The concrete was specified with a 600 microstrain and I forgot what the shrinkage test came back as but I think it would have been around there.

The joints are properly covered and shouldn't fill with debris so the shrinkage would offset any thermal expansions. The slabs were placed with a 10mm inital gap and they have grown to around 60mm now.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources