3 Phase Injection Set
Hi, is anyone aware of commercially available 3 phase injection sets for primary injection (e.g. BBP stability). Ideally currents into several kA would be required.
Thanks.
RE: 3 Phase Injection Set
Check www.smcraptor.com . This sytems may be a good and affordable solution for your requirement.
Low-voltage rental generator. Disconnect the AVR and control the field manually using a lab power supply. If you're using it as a single-phase source then disconnect or disable the negative sequence protection. Possibly easier to forget to mention to the rental company what you're going to do. You can get up to about 4kA from a 2.5MVA set, perhaps a bit more for a short period of time.