Hi Everybody!

I took some measures from a 1250_kW@480_V generator:

P:941_kW
PF: 0.87

I know that the apparent power has two components (active and reactive power) is why I am assuming that the current measured with a clamp, TC, etc. is the apparent current so if I multiply the apparent current for power factor I can get the current active component and using the triangular relationship IQ = √ ((Is ^ 2) -ip ^ 2) we can find the reactive current.

I'm pretty sure I'm doing something wrong here because:

S=P/PF=1081.6_kVA
Q=√((1081.6_kVA)^2-(941_kW)^2)=533.27_kVAR
Is=1081_kVA/(√3*480_V)=1300.9_A
IP=1300.9_A*0.87=1131.78_A
IQ=IQ=√(1300.9^2 )-(1131.78^2)=641.41_A

(IP:1131.78_A)+(IQ:641.41_A)=1773.19_A are components of IS=1330.9_A?

I appreciate any help in this regard, Greetings.

RE: APPARENT CURRENT COMPONENTS

To be short: Ip + Iq does not equal your measured current Is. Ip is a real value, Iq is an imaginary one. That is violating your first equation: Iq = √( (Is^2) - (Ip^2) )

The correct form would be Is = Ip + j*Iq, Iq will be positive or negative depending on the power factor.

RE: APPARENT CURRENT COMPONENTS

Correct:
Is=(Ip^2+Iq^2)^0.5

Incorrect:
Is=Ip+Iq

RE: APPARENT CURRENT COMPONENTS

(OP)
Thanks guys,

Following the comments of brian134 what I get is = (1131.78 + j641.41) when I transform it to polar, what I get is 1300.9 = 29.54 °, and COS (29.54 °) = 0, 87 which coincides perfectly with the vectorial composition of the active current, reactive and apparent, no problem with that.

I still wonder a few things about the subject, but I guess I have to compare the measured parameters with those resulting from mathematics because yesterday a new power factor correction panel was commissioned, the PF was directed at 1 and the current from the bank was 638_A value very close to the 641.41_A resulting from the calculation.

Thank to brian134 and wroggent for your kind help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources