Equipment Voltage Ratings
Equipment such as switchboards and panel boards have a nameplate voltage rating. Is there an allowable utilization voltage fluctuation above equipment nameplate rating?
Example would be a panel low voltage panel board is rated 208v. If I need to increase voltage on the transformer serving the panel via tap changers to compensate for voltage drop, is there a maximum voltage increase that the panel can see above it's rating? If so, what is the reference document?
Thanks.
b
RE: Equipment Voltage Ratings
The panel is probably rated 240 V.
In any event, the reference document I would suggest would be ANSI C84.1-2011. You can download a copy for free.
Thanks. What if the panel is rated 240v and I need to increase voltage 5% for voltage drop to 252v?
120/240 V is a typical nominal voltage ratings of some service panels for residential and small commercial installations. The electric utility is permitted to deliver plus and minus 5% from the nominal rating so 252 V would be OK for a 240 V panel.