Justification for use of higher GPR value

Justification for use of higher GPR value

Justification for use of higher GPR value

(OP)
Due to high resistivity value I am not able to reduce the grid resistance. Although my touch and step potentials are within limits still GPR value is higher than specified value of 5kV.

I need to convince my client that GPR of 7.8 kV is a safe value.

I have tried arguing on the point that as communication is though fiber optic cable hence this is not a problem.

I would appreciate it if someone can give more arguments backed by literature which I can cite.

RE: Justification for use of higher GPR value

I don’t think IEEE 80/2000 or IEEE 242/2001 recommends GPR to be limited up to 5 kV. In IEEE-142/2007 Ch. 4.2.6 Transferred earth potentials it is mentioned:
“The ground potential rise of a substation MAY BE on the order of some 5000 V, which may be transferred out to a nonfault location by a ground conductor (or metal pipe, rail, etc.) leaving the station.”
In my opinion, in IEEE 367/2012- IEEE Recommended Practice for Determining the Electric Power Station Ground Potential Rise and Induced Voltage from a Power Fault – Redline it could be this limitation, but I have not this standard with me.

RE: Justification for use of higher GPR value

You are not going to like my answer.

You need to work out the geographical Zone Of Influence (ZOI) and the impact of this GPR on all surrounding properties.

You can have unacceptably high GPR 'carried out' of the substation on neutrals that are externally bonded to 'remote earth' at a neighboring property's electrical service entrance, for example.

Distribution lines 'transiting' the ZOI need not be interconnected to your substation to be impacted. For example, at some distance from your substation, the worst-case GPR may be 3000V w.r.t. 'true earth' . Imagine a multi-grounded 4-wire distribution line is passing through there. The neutral will tend to rise up towards local (~3000V) earth potential, whereas a distant part of that circuit's neutral will be much closer to 0 V. Current will result.

Nice pictures in Link

Reference also at Link



Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources