VAV box flow station not reading any more

VAV box flow station not reading any more

VAV box flow station not reading any more

(OP)
I'm not sure why I can't reply to my old thread anymore. But I found the problem.

We found the pitot tubes in the VAV boxes are breaking off and therefore the pressure sensor doesn't get a reading anymore. It was a Carrier VAV box (if you want to know which product to avoid) and all the 20 or so VAV boxes are affected. We replaced one with an Accutrol Airvalve and that works perfectly.

After seeing this I wonder how many million VAV systems turned into CV systems by that? but I definitely don't want to use VAV boxes anymore (not after seeing an airvalve)

RE: VAV box flow station not reading any more

Thanks for providing the end result! I was interested in this thread before.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources