Jobs

Relief Valve Capacity

Relief Valve Capacity

Relief Valve Capacity

(OP)
We are being asked to change out all schedule 80 pipe nipples to Double X nipples. The ID of the nipples will be substantially smaller. If the nipple is on the inlet side of the relief, will it affect the capacity of the relief?

RE: Relief Valve Capacity

It can. It depends on the PSV, the scenario, and the pipe and fittings.

Good luck,
Latexman

Technically, the glass is always full - 1/2 air and 1/2 water.

RE: Relief Valve Capacity

(OP)
Natural gas plant, discharge piping on a compressor, 1" weldalet, 1" AG relief valve, 985 psig MAOP, minimal discharge piping. Will a double x fitting change the relief capacity? Where do I find written proof either way?

RE: Relief Valve Capacity

It's not as simple as that IMO. You won't find written proof anywhere, since it is specific to your PSV, the scenario, and the pipe and fittings. Someone knowledgeable in reliefs will have to calculate and document that it is okay, or specify the modifications needed. Basically, the inlet pressure drop (and this probably includes more pipe and fittings than just the subject nipple) should be less than 3% of set pressure at rated flow.

Good luck,
Latexman

Technically, the glass is always full - 1/2 air and 1/2 water.

RE: Relief Valve Capacity

API 520 Part 1 and Part 2 and API 521 should give you most of what you need to do it, especially API 520 Part 2.

Good luck,
Latexman

Technically, the glass is always full - 1/2 air and 1/2 water.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources