Galvanized Angle and Stainless Steel Anchors
I have a condition where I need to bolt a steel angle to concrete. This angle will hole up a floor. It is a location on the inside of a cut off wall (fresh water). The wall will leak a little, but for design I am assuming it will be wet for long periods of time. I don't like epoxy for sustained tension loads so I am looking at expansion bolts.
The angle will be galvanized. The cracked concrete approved anchors available appear to be stainless. The is a galvanic corrosion condition with this condition, but most of what I can find indicates it is not a concern except in some marine conditions. While I don't think this qualifies as marine, I do think it is worse than your average exterior application.
What do you all think about the corrosion potential for this?
RE: Galvanized Angle and Stainless Steel Anchors
I think it is fine. The anchors won't corrode, and while there may be a small area of corrosion in the angle at the anchor location, I would not be concerned.
DaveAtkins
X2. See page 25 of this document: Link. According to Hilti:
1) A galvanized substrate is ok with any kind of fastener.
2) A stainless steel fastener is okay with any kind of substrate.
This is from the perspective of fastener corrosion only. I believe that the substrate is assumed to be ok by virtue of the ratio of anode to cathode argument.
Agree with above...have used many times for aluminum and galvanized anchorage.
Thanks all.
I don;t have a problem with it, but it seems those pesky galvanic potential charts always say the sky is falling.