Construction Joint of vehicular ramp of car parking
To all experienced construction engineers,
Our contractor wants to place the construction joint of ramp beam at the face of column support due to work difficulty if it is done monolithically. Is it safe to place the joint at the face of support? What provisions to be made if such joint is placed at the face of support? Please give your opinion on this issue. Thank you.
RE: Construction Joint of vehicular ramp of car parking
Attached is the plan of ramp beam
Definitely something you can allow; Just make sure they use proper detailing with a key and steel accross the joint, ideally plus a roughened surface, or (alternatively) design and detail for an expansion joint.
Personally I would never put an expansion joint at a change in grade or slope, unless absolutely unavoidable.
- Small bars to be site bent (pain in the butt, but very simple)
- Spiral stirrup & links
- Drossbach ducts
- Threadbare & Couplers
- Elephant foot ferrules
- Embedded steel beam & joint
- Weld plates
Can they not stop the column at the transverse ramp beam soffit and run the beam over the top of the column, then continue the column on up? Is that not the way it is usually done at transverse ramp beams? Seems much better than placing a joint at the column face.
I'm with AJK here in that I think that shear friction is a high priority. And that means top steel properly anchored within the columns to develop fy and to transfer tension back down to the beam compression zone. Hence my concern above regarding constructibility of the joint.
...6.4.4 — Construction joints in floors shall be located
within the middle third of spans of slabs, beams, and
girders.
The idea of AJK is good, but ramp beam will land at the floor deck connecting the ramp. what we are going to do,
is put extra bars across the joint on both sides extending to the mid span of the beams adjacent to the column.
1- Check shear friction and get reinforcement required ,this reinforcement is not added to what required for bending , you should use the bigger
2- Before second poor is cast , make sure surface is rough to Amplitude 5 mm and old concrete surface is free debris and wet the surface (hydrate the concrete
3- Some contractors use bonding agent (which i do not believe is much useful)
I will see your "not useful" and raise you a "dangerous bond breaker when applied incorrectly".
Surface Saturated Dry (SSD) remains the gold standard for good reason...