Highest rating for 11kV switchboard.

Highest rating for 11kV switchboard.

Highest rating for 11kV switchboard.

(OP)
Hi-
I am looking for a switchboard produced after IEC62271-200 for an 50Hz - 11kV offshore installation.
General limit for most vendors seem to be 4000A nominal and 50/125kA short-circuit.

Does anyone know a vendor with higher values on one or both parameters which has a reference list for offshore projects?

Best regards
Preben Jakobsen

RE: Highest rating for 11kV switchboard.

Schneider-Electrics PIX-H switchgear is one. Don't know if they have any references to offshore, you'll have to ask Schneider.

RE: Highest rating for 11kV switchboard.

I don't think PIX-H exceeds the OP's stated values, does it? The only MV products I'm aware of which exceed those ratings aren't distribution-class breakers, they're for generator duty and have thermal ratings of 12kA or more, with fault withstand of 72/200kA or more. Siemens VB1 / HB1 series are typical of the type.

What's the application? You're looking for unusually high ratings - is it time to consider a jump to the next voltage band, or splitting the board into two? In an offshore application with on-board generation be very careful if you're using distribution-class VCBs in generator applications because they can't handle the severe breaking conditions caused by the high X/R ratio and long time to first current zero. The interruptors burn away due to the persistent arc, then fail.

RE: Highest rating for 11kV switchboard.

(OP)
Hi ScottyUK
I am in the early phase of a platform design and is on the limit of the 76 MVA that is a result of 11 kV and 4000 A. And when the project develops the load normally increases.
I would like to keep 11 kV and connect the generators directly to the main SWBD and I also would like to have all generators on same SWBD as it gives me flexibility: In the early phase when the load is high it will be easyer to maintain generators and in the later phase when load might decrease I am able to run only the required no. of generators.
I am aware that i can't assume the standard T=45ms and that I can't utilize the full rating of the SWBDs. In the current design i have included Is limmiters.

Right now I have a compact and light design which is important offshore. If i know it is possible to have 5000A it gives me pease in mind.
Datasheets for PIX-H gives that value (with fan cooling).

Best regards
Preben Jakobsen

RE: Highest rating for 11kV switchboard.

Siemens 8DA10 / 8DB10 range has a 5000A thermal rating but falls a little short on the fault rating - 40kA / 3sec. It's a gas-insulated bus so it should survive the offshore environment well, and being GIS it is very compact.

I admit that I'm slightly biased against some of the old Areva designs - which now a Schneider badge - because the quality control hasn't always been as good as it could be. I don't have specific experience of the PIX range, so it might be better than the stuff I have worked with.

RE: Highest rating for 11kV switchboard.

Not that I advocate the Schneider switchgear, but it does exceed current rating, it's up to 5000A.
Link

RE: Highest rating for 11kV switchboard.

Thanks ShooterBlooter, that option wasn't shown in my old Area data. smile

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources