A confusion of terms is present here. For the wall you apparently are planning, the use of the term "limestone" in the USA would imply stone cut from a quarry, with rough sides. For that usage and as a retaining wall, no mortared joints are used. For a masonry block wall, your "reconstituted limestone", which, for me, is an entirely different wall material maybe use mortar. For the masonry wall the change in temperature of the wall would be affected by the "heat sink" effect of those blocks farther back from the face. That makes the change in dimensions of the face less likely. That,then, would call for a longer spacing of control joints than for a single block depth (front to back). Masonry walls in a building typically require a joint spacing for temperature effect between 15 and 30 feet, averaging at 20 feet. An earth retaining wall has much less effect of temperature change in the area. Thus, for your wall, I'd set that spacing at 30 feet or more. roughly 10 meters. This is similar to AASHTO specs for cantilever and gravity retaining walls. However, if no mortar is used, I'd omit the control joints for the same reason given in my first post.