Balanced external static pressure question

Balanced external static pressure question

Balanced external static pressure question

(OP)

I have a 3 ton package heat pump system and have a question about External Static Pressure. The system list a max ESP 0.5 iwc. My measured ESP is .42 iwc, which includes 0.25 of the return filter. The thing I'm finding strange is the entire ESP is in the return duct, with the supply duct barely registering and back pressure unless I start closing down registers. Is this unbalanced situation an issue and why?

RE: Balanced external static pressure question

When talking about duct pressure, you need to note specific location, it is different at each position on each duct. The closer you are to the atmosphere, the less pressure difference compared to atmosphere - and the final difference equals terminal unit pressure drop.

That by itself has nothing to do with balancing.

RE: Balanced external static pressure question

All you have to do to reach rating is have the correct air volume.

If your pressure is at or below rated pressure, the machine should work as cataloged......it doesn't care if the pressure drop is in the supply or return.

RE: Balanced external static pressure question

(OP)
Thanks for the responses. With this unit being a package system, the recommended location for testing ESP is in the ducts just as they leave or enter the the system.
At the pressures that I am measuring and referring to the blower performance data charts, the system should be delivering right at 1200 CFM with a clean filter, so it sounds like I can relax and not worry about the differences.
I just wasn't sure if the load on the blower would be less or more with all of the work being pulling and none pushing air through the system.

RE: Balanced external static pressure question

Consider the physics......how can it take more hp to pull than push the sqame load?

A brush-up in basic physics may be in order.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources