For a 110VAC CTE system, there's an earth connection between the 2 leads of the output transformer. this splits the 100V out to +55V and -55V. It means the voltage between live and earth is always limited to 55V.

I have a 2P+E socket and i'm wondering if I should connect the earth or not giving that there's one upstream in the transformer. Can someone provide a typical working diagram for CTE terminations please. That'd be helpful.

RE: 110VAC Centre Tapped Earth (CTE)

The earth terminal on a receptacle is used to connect to, and ground metal cases of appliances, tools and equipment connected to the receptacle. The reason is so that any internal fault that may cause a voltage on exposed metal parts of items will have a low impedance path back to the source and provide protection by causing the circuit protective device (fuse or circuit breaker) to open. For this reason the earth terminal should be connected in such a way as to provide a low impedance path back to the supply transformer. The method of connection is subject to local codes. This is an international forum. Post your location and someone local may give more specific guidance.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 110VAC Centre Tapped Earth (CTE)

(OP)
Bill,

Thanks for the response. I'm in the UK so BS standard should apply.

RE: 110VAC Centre Tapped Earth (CTE)

Vince,


Absolutely connect the earth at the transformer to the earth sleeve of the 110V socket.

Have a look at http://www.blakley.co.uk/sites/default/files/Trans... - sketch (iv) on page 2 shows the connections relevant to your transformer.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources