UPS Maintenance
UPS Maintenance
UPS Maintenance
Hi all,
What are the recommended UPS maintenance? Here i am referring to Inverters and Chargers only.
We are using AEG Saft Protect Inverters and Profitec Chargers. They consists of mainly electronics cards, capacitors and the usual. I am not too sure how to maintain a system that depend mainly on electronic cards.
I heard before that harmonic measurement is one sapect of UPS maintenance, but how important is it?
Please help, thanks!
RE: UPS Maintenance
First, check the manufacturer's instruction manual.  There is usually a section on recommended maintenance.
Otherwise, some of the following may help:
1. Perform a general visual inspection to look for the obvious such as: smoky deposits, odor, charred parts, arcing contacts or connections, loose connections, noisy cooling fan motor, or leaky blistered capacitors.
2.  Yearly do a infrared scan.
3.  Monthly check the ac ripple on the dc voltage output of the battery charger (will give indication of capacitor breakdown and/or firing circuit problems).
4.  Clean units to keep dust build up to a minimum. (heat is an enemy of electronics)
that's a start.
wbd
RE: UPS Maintenance
hi..
is the supplier or manufacturer offers maintenance agreement?...sometimes it is worth getting it aside from the regular maintenance work you can see on the manual..
dydt
RE: UPS Maintenance
hi
One thing more,
usage of Termo cam as a conditmonitoring action can be usefull.
saeed
RE: UPS Maintenance
If you only have 1 unit it is probaly best to have the manufactur do the service. If you have more, most of the suppliers have a day or 2 school for maintenance training.
Checking the semi conductors for leakage current ( scr or xistors) is one way to find components that may need replacing before a compleate failour.