What is the min. splice length for reinforcing in masonry? Where is this information? Either it isn't in ACI 530, or I skipped right over it.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Masonry Reinforcing
DaveAtkins
RE: Masonry Reinforcing
thanks again
RE: Masonry Reinforcing
Good luck
RE: Masonry Reinforcing
RE: Masonry Reinforcing
RE: Masonry Reinforcing
To find this out, read ACI 530 closely.
I hope this helps
RE: Masonry Reinforcing
I always call out an extra 3" to 6" inches of lap, depending on the height of the wall, between the dowels coming out of the footing and wall reinforcment. The reason I do this is, depending on how sloppy the mason is, there can be a significant amount of mortar that falls down the cells prior to grouting the wall.
Chip
RE: Masonry Reinforcing
This is one of the reasons you have clean outs at the bottom of the walls/lifts. Before the cells are filled, you can inspect them. Also you can inspect them after the grout is placed to confirm solid core grouting.