Breaker Column Failure Protection for 500kV Live tank Breakers

Breaker Column Failure Protection for 500kV Live tank Breakers

Breaker Column Failure Protection for 500kV Live tank Breakers

(OP)
Can someone please explain what Breaker column failure is, and how does this protection work.

RE: Breaker Column Failure Protection for 500kV Live tank Breakers

I presume that you are referring to a live tank circuit breaker design.
"On live-tank circuit breakers, the interrupter chamber is arranged in the insulator, which can be either porcelain or of a composite material and is at high potential with the voltage level determining the length of the insulators for the interrupter chamber and the insulator column."

You can Google for "live tank breaker" vs. dead tank breaker design and check on image to see the insulator column.

RE: Breaker Column Failure Protection for 500kV Live tank Breakers

Basic idea is to put a current transformer around the leg supporting the breaker in such a way as to detect fault currents and trip the equipment out of service. From here it just gets more sophisticated as this elemented is integrated into the larger protection scheme.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Breaker Column Failure Protection for 500kV Live tank Breakers


The concept of using CT on the base of insulator it is common practice for dead-tank breakers design. However for live tank breakers LTB design virtually impossible difficult at best since there is not current flow at the base of the LTB breaker insulator.
If any one have information with LTB with CT as described above post please share that with us

RE: Breaker Column Failure Protection for 500kV Live tank Breakers

This is more commonly known as Breaker Frame Leakage protection. Use a donut CT mounted on the bottom of the structure.... Run your ground connection plus any control cables through this CT and connect it to an overcurrent relay. Simple and effective.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources